@BRRABill Yup, sure is. To be honest, if you're just powering computers it makes very little difference. You could actually feed the computers pure DC (no AC sine wave) and they'd work just fine. Where you get into trouble is stuff like electric motors, air conditioners, anything that plugs straight into the wall without a power supply (wall wart).
-
You can buy DC powered servers. They create less heat and suck less overall power.
-
@scottalanmiller said:
You can buy DC powered servers. They create less heat and suck less overall power.
whoa, TIL
-
What do you think about the "S" line versus the "P" line.
Big cost savings.
-
@BRRABill said:
What do you think about the "S" line versus the "P" line.
Big cost savings.
The P line has 2 distinct output groups. The S does not. Basically a feature you may or may not desire or need. Personally, I would skip it and go with the S as long as it works with their software. The software monitoring account for a lot IMO.
-
I'm probably going to do that, go with the S.
What is the advantage of "2 distinct output groups"?
-
@BRRABill said:
What is the advantage of "2 distinct output groups"?
Is it bad manners to quote oneself? LOL.
Or not advantage, but reasoning why it would be used?
-
- For monitoring distinctly. Very useful if you have different devices plugged in to know their power levels explicitly.
-
@JaredBusch said:
- For monitoring distinctly. Very useful if you have different devices plugged in to know their power levels explicitly.
I researched this a bit on their site. Pretty cool.
Monitors on one side, shutting down sooner.
Interesting concept.
-
@scottalanmiller said:
The recommended design is two UPS, one for each rail. Each PSU goes into one rail, each rail into one UPS each UPS into as separate circuits as you can get.
What do you mean by "rail" here?
-
@BRRABill said:
@scottalanmiller said:
The recommended design is two UPS, one for each rail. Each PSU goes into one rail, each rail into one UPS each UPS into as separate circuits as you can get.
What do you mean by "rail" here?
In this sense, rail means the left or right rear post of the server rack. A lot of server racks have a power bar going up and down the rails.
-
@JaredBusch said:
In this sense, rail means the left or right rear post of the server rack. A lot of server racks have a power bar going up and down the rails.
Thanks.
We are all tower servers here.
The only rack we have here is an equipment rack.
Man, I need a road trip to some of the places you guys work.
-
@JaredBusch said:
In this sense, rail means the left or right rear post of the server rack. A lot of server racks have a power bar going up and down the rails.
So, multiple servers could be plugged into each rail?
So @scottalanmiller is saying the recommended solution is to plug all server into one side of the rack (rail), and then that rail itself into a UPS?
That would seem hard to calculate the proper wattage unless the rack was full.
-
@BRRABill said:
@JaredBusch said:
In this sense, rail means the left or right rear post of the server rack. A lot of server racks have a power bar going up and down the rails.
Thanks.
We are all tower servers here.
The only rack we have here is an equipment rack.
Man, I need a road trip to some of the places you guys work.
Most SMB do not have them. It is a term from Enterprise and colocation datacenters.
Since you have 2 power supplies in your servers, you plug PS1 into the left rial and PS2 into the right rail on all your hardware.
You plug the left rail into one UPS and the right rail into a different UPS. Then each UPS is also plugged into a different circuit. -
@BRRABill said:
@JaredBusch said:
In this sense, rail means the left or right rear post of the server rack. A lot of server racks have a power bar going up and down the rails.
So, multiple servers could be plugged into each rail?
So @scottalanmiller is saying the recommended solution is to plug all server into one side of the rack (rail), and then that rail itself into a UPS?
That would seem hard to calculate the proper wattage unless the rack was full.
Why would it be hard? You know that you plugged in 4 servers into each rail. Each PS is 500W. So each rail has 2kW.
-
@BRRABill said:
Man, I need a road trip to some of the places you guys work.
You and me both, I think it'd be an eye opening experience for everyone
-
@JaredBusch said:
Why would it be hard? You know that you plugged in 4 servers into each rail. Each PS is 500W. So each rail has 2kW.
Do you always have each rack pre-filled with servers?
I was thinking where you had 1 server or 2 in a rack. Do you buy capacity for now, or when the rack is filled?
-
@MattSpeller said:
You and me both, I think it'd be an eye opening experience for everyone
I'm lucky that my wife (also in IT) has always worked in larger environments. So I get to see a lot of "the other side" in my little SOHO world.
-
@BRRABill said:
@JaredBusch said:
Why would it be hard? You know that you plugged in 4 servers into each rail. Each PS is 500W. So each rail has 2kW.
Do you always have each rack pre-filled with servers?
I was thinking where you had 1 server or 2 in a rack. Do you buy capacity for now, or when the rack is filled?
You plan your capacity on what you have or realistically expect to get in the near term. always. You don't plan for some unknown future amount of servers.
-
@BRRABill said:
@JaredBusch said:
Why would it be hard? You know that you plugged in 4 servers into each rail. Each PS is 500W. So each rail has 2kW.
Do you always have each rack pre-filled with servers?
I was thinking where you had 1 server or 2 in a rack. Do you buy capacity for now, or when the rack is filled?
For UPS it's best to talk to the business and see what their plans are. You know you need batteries for the things every 3 years and that's a good time to swap out if you need bigger (bigger being the only real reason to change UPS).