ML
    • Recent
    • Categories
    • Tags
    • Popular
    • Users
    • Groups
    • Register
    • Login

    EATON AMA

    IT Discussion
    eaton ama
    25
    208
    118.8k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • art_of_shredA
      art_of_shred Banned @coliver
      last edited by

      @coliver said:

      @JColeKen said:

      @art_of_shred Actual operating load is the most practical.

      How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?

      An ammeter works great if you have one and want real numbers.

      scottalanmillerS windsoW 2 Replies Last reply Reply Quote 1
      • JColeKenJ
        JColeKen Vendor @art_of_shred
        last edited by

        @art_of_shred 70-80% is a safe bet. Sometimes it is lower, but that is typically what I default to when sizing.

        1 Reply Last reply Reply Quote 2
        • scottalanmillerS
          scottalanmiller @art_of_shred
          last edited by

          @art_of_shred said:

          @coliver said:

          @JColeKen said:

          @art_of_shred Actual operating load is the most practical.

          How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?

          An ammeter works great if you have one and want real numbers.

          Even in the afternoon or do you have to switch to a PMmeter?

          JColeKenJ art_of_shredA 2 Replies Last reply Reply Quote 1
          • windsoW
            windso Vendor @art_of_shred
            last edited by windso

            @art_of_shred @coliver

            Yes! These can be somewhat inexpensive. We usually see IT equipment running at 60% or less of nameplate rating. The challenge we have when sizing a UPS or PDU, and you will have too, is that generic rules always bite you at some point. If you are the exception, you risk taking down everything.

            Keep in mind that sizing a UPS or PDU at less than 80% or 100% utilization is a good thing. UPSs and PDUs are like the breakers feeding your Christmas tree lights - Once you add too much, the lights go off!

            art_of_shredA 1 Reply Last reply Reply Quote 3
            • JColeKenJ
              JColeKen Vendor @scottalanmiller
              last edited by

              @scottalanmiller Lolz

              1 Reply Last reply Reply Quote 1
              • art_of_shredA
                art_of_shred Banned @scottalanmiller
                last edited by

                @scottalanmiller said:

                @art_of_shred said:

                @coliver said:

                @JColeKen said:

                @art_of_shred Actual operating load is the most practical.

                How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?

                An ammeter works great if you have one and want real numbers.

                Even in the afternoon or do you have to switch to a PMmeter?

                Once again sporting your prowess in all things electrical. I defer to your expertise...

                1 Reply Last reply Reply Quote 1
                • NicN
                  Nic
                  last edited by

                  Couple of ones that might be more home oriented than business:

                  1. Do you have any plans to get into the home battery market, like Tesla? (or are you already) These are the backup batteries that you can charge from solar and then power your home from (or use as a backup for if the power is out).
                  2. What would you recommend in the prosumer market for IT pros or technically minded folks to use at home?
                  windsoW 1 Reply Last reply Reply Quote 4
                  • art_of_shredA
                    art_of_shred Banned @windso
                    last edited by

                    @windso said:

                    @art_of_shred @coliver

                    Yes! These can be somewhat inexpensive. We usually see loads running at 60% or less of nameplate rating. The challenge we have, and you will have too, is that generic rules always bite you at some point. If you are the exception, you risk taking down everything.

                    Keep in mind that sizing a circuit at less than 80% or 100% is a good thing. You never want to completely oversize, but UPSs and PDUs are like the breakers feeding your Christmas tree lights - Once you add too much, the lights go off!

                    Just to clarify, I thought that was worded a little confusingly. You never want your load to equal or surpass your protection. Ideally, your expected amp load should only be about 80% of your protection's full capacity. Otherwise, you can exceed its ability to protect and either diminish its performance or nullify the protection altogether.

                    windsoW 1 Reply Last reply Reply Quote 2
                    • art_of_shredA
                      art_of_shred Banned
                      last edited by

                      That didn't sound good when I read it, so keep your mind out of the gutter.

                      scottalanmillerS 1 Reply Last reply Reply Quote 0
                      • scottalanmillerS
                        scottalanmiller @art_of_shred
                        last edited by

                        @art_of_shred said:

                        That didn't sound good when I read it, so keep your mind out of the gutter.

                        Too late.

                        1 Reply Last reply Reply Quote 0
                        • dafyreD
                          dafyre
                          last edited by

                          Are any of your PDUs capable of being remotely managed? So we can power stuff on / off remotely?

                          mdecampM 1 Reply Last reply Reply Quote 2
                          • J
                            Jason Banned
                            last edited by

                            Do you offer and trade in discounts for large UPSs to switch to Eaton? We currently have Liebert 3 Phase UPS systems.

                            mdecampM 1 Reply Last reply Reply Quote 1
                            • MattSpellerM
                              MattSpeller
                              last edited by

                              • What do you see as the future of battery technology in UPS units? Does lead acid still have a future in these kinds of applications?

                              • Looking ahead 10 years what do you see as potentially disruptive technologies that might enter your field?

                              • Of your products, is there any one you or the company is particularly proud of? Why?

                              • The core of your business is design of power supplies - have you ever considered making consumer/"prosumer" ATX power supplies?

                              windsoW 1 Reply Last reply Reply Quote 2
                              • mdecampM
                                mdecamp Vendor @dafyre
                                last edited by

                                @dafyre

                                @dafyre said:

                                Are any of your PDUs capable of being remotely managed? So we can power stuff on / off remotely?

                                Yes. Here's a closer look at our third generation of rack PDUs: http://powerquality.eaton.com/Products-services/Power-Distribution/ePDU/interact/,

                                1 Reply Last reply Reply Quote 1
                                • mdecampM
                                  mdecamp Vendor @Jason
                                  last edited by

                                  @Jason said:

                                  Do you offer and trade in discounts for large UPSs to switch to Eaton? We currently have Liebert 3 Phase UPS systems.

                                  We don't have a formal program--too many variables to factor in for the larger systems. We can certainly connect you with someone local to discuss and/or provide a quote.

                                  1 Reply Last reply Reply Quote 1
                                  • windsoW
                                    windso Vendor @MattSpeller
                                    last edited by windso

                                    @MattSpeller - My take:

                                    Lithium based technologies are great, but who knows how soon they'll come down in price. They're still expensive, many lithium technologies are flammable, and transportation and shipping are becoming more difficult.

                                    There are many 10-year outlooks ahead. The good news is that batteries and energy storage have global research focus from both industry and governments. This should mean the industry will see some major changes in the years to come.

                                    We're really proud of our Intelligent Power Manager (IPM) software. It continues to change the game about how power interacts with IT. We're the first to integrate with virtualization platforms to help manage the virtualization space rather than the physical server alone. We've loved the response from users in the community using these powerful tools and we will continue to provide more benefits in the months to come. Eaton.com/virtualization

                                    The core of our business isn't necessarily power supplies, but power management, a true statement whether it's fuel deliver systems for airplanes, superchargers for top vehicle performance, or UPSs and distribution for datacenters and IT closets. ATX, pro-sumer power supplies are a little out of our focus. We want to position ourselves with products that can improve functionality and interaction for companies that make business happen.

                                    1 Reply Last reply Reply Quote 4
                                    • windsoW
                                      windso Vendor @Nic
                                      last edited by

                                      @Nic The home battery market...

                                      1. I think Tesla's play is more on how to re-purpose used automotive batteries, which is still a good thing. The Powerwall is a great step forward for the Grid, but there are a lot barriers to make this an attractive market outside of California and Hawaii.

                                      2. Prosumer market is a tough one. More consumers are shifting to laptops, and far less dependent on peripherals like printers or dedicated monitors these days. That brings to mind the question, why need a battery for basic home use? For people running dedicated servers at home, we certainly have the technology at the right price to keep you up and running. I think the prosumer market has been moving away from battery backup for a while and will continue to do so as technology advances.

                                      NicN 1 Reply Last reply Reply Quote 7
                                      • windsoW
                                        windso Vendor @art_of_shred
                                        last edited by

                                        @art_of_shred, Well said!

                                        1 Reply Last reply Reply Quote 0
                                        • DashrenderD
                                          Dashrender @mdecamp
                                          last edited by

                                          @mdecamp said:

                                          @IRJ Very comparable when it comes to price and functionality. We do offer a 3-year warranty that covers the entire UPS and the battery: http://powerquality.eaton.com/Products-services/Backup-Power-UPS/3S.aspx?cx=3

                                          Typical desktop models:
                                          Eaton 3S: http://powerquality.eaton.com/Products-services/Backup-Power-UPS/3S.aspx?cx=3
                                          Eaton 5S: http://powerquality.eaton.com/Products-services/Backup-Power-UPS/5S.aspx?cx=3

                                          The 5S has a nice LCD screen.

                                          We just had a 2.5 hour outage yesterday and I hadn't replaced my desktop UPS yet. I'm ordering this right now (Amazon has it for $200 for the 1500 model.. awesome price!)

                                          scottalanmillerS BRRABillB 2 Replies Last reply Reply Quote 6
                                          • BRRABillB
                                            BRRABill @BRRABill
                                            last edited by

                                            @BRRABill said:

                                            Could you give some details, say, in the difference between the 5S1500 and the 5P1500 that might sway a person either way?

                                            Just throwing this back up there in case it was missed...

                                            1 Reply Last reply Reply Quote 1
                                            • 1
                                            • 2
                                            • 6
                                            • 7
                                            • 8
                                            • 9
                                            • 10
                                            • 11
                                            • 8 / 11
                                            • First post
                                              Last post