ML
    • Recent
    • Categories
    • Tags
    • Popular
    • Users
    • Groups
    • Register
    • Login

    EATON AMA

    IT Discussion
    eaton ama
    25
    208
    118.9k
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • mollyM
      molly Vendor @BRRABill
      last edited by

      @BRRABill no complaints about the season so far 12-0! http://thesource.com/wp-content/uploads/2015/11/newton-dab.jpg

      1 Reply Last reply Reply Quote 0
      • dafyreD
        dafyre @JColeKen
        last edited by

        @JColeKen Are thsoe probes also available via SNMP?

        JColeKenJ 1 Reply Last reply Reply Quote 1
        • mdecampM
          mdecamp Vendor @JaredBusch
          last edited by

          @JaredBusch said:

          Eaton is a huge company now with a lot more products than UPS devices.

          But as most of that is power related, the SMB IT managers have no real use for it.

          What other products does Eaton have that would be good for the SMB IT people to know about.

          Rack PDUs, rack/enclosures/cages, airflow management, power management software, environmental monitoring, maintenance services, remote monitoring, surge protection, power factor correction, etc.

          1 Reply Last reply Reply Quote 1
          • gbeyhautG
            gbeyhaut @JaredBusch
            last edited by

            @JaredBusch PDU's, racks, are definitely in the wheel house of SMB IT. We also have panel boards (breaker panels) , surge protection, and LED lighting.

            JaredBuschJ 1 Reply Last reply Reply Quote 2
            • JaredBuschJ
              JaredBusch @gbeyhaut
              last edited by

              @gbeyhaut @mdecamp Since the B-Line acquisition, do you also have sever cabinets? They used to make some but I have not heard of them recently.

              gbeyhautG 1 Reply Last reply Reply Quote 0
              • JColeKenJ
                JColeKen Vendor @dafyre
                last edited by

                @dafyre Yes, that one I linked ties directly into the web card of the UPS. It is accessible via SNMP that way. We also have one for our PDU offering.

                1 Reply Last reply Reply Quote 0
                • gjacobseG
                  gjacobse
                  last edited by

                  How frequently do you check and/or test your UPS batteries?

                  windsoW JColeKenJ 2 Replies Last reply Reply Quote 0
                  • mdecampM
                    mdecamp Vendor @dafyre
                    last edited by

                    @dafyre said:

                    Maybe I missed this in the post by @mdecamp -- But do you guys recommend any Generator companies over another? Or do you build generators yourselves?

                    We do have our own line of generators (primarily residential): http://generatorcalculator.eaton.com/ We don't really recommend a generator company for business applications.

                    JaredBuschJ 1 Reply Last reply Reply Quote 0
                    • ciwoodhouseC
                      ciwoodhouse @BRRABill
                      last edited by

                      @BRRABill Here's the gist:
                      • You can purchase up to three times the VA you are trading in! The new Eaton unit can be a smaller VA rating than the old UPS too.
                      • Your discount is for the purchase of the new Eaton UPS only and not the old UPS traded in
                      • Return shipping labels will be provided to you to send the old UPS(s) back for disposal – free of charge

                      BRRABillB 1 Reply Last reply Reply Quote 0
                      • gbeyhautG
                        gbeyhaut @JaredBusch
                        last edited by

                        @JaredBusch check out @JColeKen's baby www.eaton.com/rackpack

                        JaredBuschJ 1 Reply Last reply Reply Quote 1
                        • JoyJ
                          Joy
                          last edited by

                          @gbeyhaut Do you have office here in The Philippines?
                          Would love to recommend your product to my Manager in the future.

                          gbeyhautG 1 Reply Last reply Reply Quote 1
                          • windsoW
                            windso Vendor @gjacobse
                            last edited by

                            @gjacobse

                            We have ABM, an advanced method or charging batteries. It does an automatic self check every 30 days. It also turns the charger off when it is not needed so you keep your batteries cool and prolong their lifespan.

                            gjacobseG 1 Reply Last reply Reply Quote 4
                            • mdecampM
                              mdecamp Vendor @coliver
                              last edited by

                              @coliver said:

                              @mdecamp said:

                              @gjacobse said:

                              Using a UPS is a short term option. In some cases services need to be maintained longer -

                              Are there best practices for deploying a UPS with a generator?

                              When designing with a backup solution, compatibility between a UPS and Generator is usually one of the biggest issues. It can be complex and confusing.

                              If the generator isn't sized large enough, it may not be able to hold voltage and frequency within input tolerances when the UPS comes online. The UPS will view the generator as an unstable power source and never come off of battery. The UPS will have a set input voltage and frequency window; if you go outside the window the UPS will go on battery. You can get into a vicious cycle of going on and off of battery until your UPS crashes and your IT load are dropped.

                              Several reasons why the generator would be an issue:
                              • The generator is like a car engine. As it maintains RPMs, it maintains frequency. When the UPS transfers from battery to generator power, the engine may slow down a bit. You can compare this to driving a stick shift while stopped at a red light headed uphill. When you dump the clutch, if you aren't giving it enough gas (or if you are driving a pinto) the RPMs are going to drop down.
                              • Just like in the automotive world, the bigger the engine (generator here) the more it can handle the dumping of the clutch as the UPS comes off of battery. Bigger (aside from your budget number) is better
                              • Natural Gas is usually the least combustible fuel out there, and generators that run off of NG are slow to respond and may need to be sized larger than propane counterparts. Diesel is best, but usually predominant in the world of 50kW and larger, but it may present a lot more budget and maintenance issues if you don't have a maintenance program or run them weekly, etc.
                              • When looking at smaller generators (30kW and below) look at the governor. Electronic governors are quick to respond, mechanical governors are not and may add headaches.
                              The features of the UPS can also impact you configuration. Most single phase UPS products (20kVA and below) will come back online all at once. Larger three phase UPS products will have "current walk-in" and will slowly transition from battery anywhere from 5-60 seconds. As for sizing solutions with generators under 30kVA for single phase UPS applications, I usually lean on the err of caution being a manufacturer. We recommend the same if you are responsible as the decision maker.
                              • Generator should be sized 2 times the total load (UPS, A/C, an everything else) for NG and mechanical governor
                              • 1.5 times the load will work if you have a new generator, Propane or Diesel and an electronic governor.
                              • Any mix from the above puts you somewhere in the middle of 1.5 to 2 times.

                              This was an amazing explanation and answered a few of my questions. Thank you.

                              Full disclosure is that I stole this post from @windso

                              art_of_shredA 1 Reply Last reply Reply Quote 1
                              • JColeKenJ
                                JColeKen Vendor @gjacobse
                                last edited by

                                @gjacobse Our UPS units run a battery test every 30 days, set standard from the factory. If you prefer, you can increase the frequency. Utilizing the software can also provide you a live look at your current battery capacity.

                                1 Reply Last reply Reply Quote 2
                                • gbeyhautG
                                  gbeyhaut @Joy
                                  last edited by

                                  @Joy we do have offices there. I'll try and connect you with someone.

                                  JoyJ 1 Reply Last reply Reply Quote 0
                                  • JaredBuschJ
                                    JaredBusch @mdecamp
                                    last edited by

                                    @mdecamp said:

                                    @dafyre said:

                                    Maybe I missed this in the post by @mdecamp -- But do you guys recommend any Generator companies over another? Or do you build generators yourselves?

                                    We do have our own line of generators (primarily residential): http://generatorcalculator.eaton.com/ We don't really recommend a generator company for business applications.

                                    Boo 😞 no price after clicking all the things.. Sorry Eaton, that is a huge ass fail. Give me MSRP at least and say get a quote just for your or somethying...

                                    https://i.imgur.com/hiBd9dY.jpg

                                    gbeyhautG JColeKenJ 2 Replies Last reply Reply Quote 3
                                    • JoyJ
                                      Joy @gbeyhaut
                                      last edited by

                                      @gbeyhaut said:

                                      @Joy we do have offices there. I'll try and connect you with someone.

                                      Great, Thanks in advance.

                                      1 Reply Last reply Reply Quote 0
                                      • gjacobseG
                                        gjacobse @windso
                                        last edited by

                                        @windso @JColeKen

                                        ABM - Advance Battery Management ?

                                        Having a smart charger that can turn itself off/on as needed can increase battery life. Part of what kills batteries other than time and use is heat. I can't tell you the number of SLA or AGM batteries I have replaced due to being 'cooked' by over voltage.

                                        mollyM JColeKenJ 2 Replies Last reply Reply Quote 0
                                        • JaredBuschJ
                                          JaredBusch @gbeyhaut
                                          last edited by

                                          @gbeyhaut said:

                                          @JaredBusch check out @JColeKen's baby www.eaton.com/rackpack

                                          That is sweet. exactly what I was looking for.

                                          1 Reply Last reply Reply Quote 1
                                          • gbeyhautG
                                            gbeyhaut @JaredBusch
                                            last edited by

                                            @JaredBusch prices on the web!! NEVER! www.cdw.com should have some prices. To be honest we sell these primarily through electrical distributors like Wesco and Rexel.

                                            JaredBuschJ scottalanmillerS 2 Replies Last reply Reply Quote 0
                                            • 1
                                            • 2
                                            • 3
                                            • 4
                                            • 5
                                            • 6
                                            • 7
                                            • 10
                                            • 11
                                            • 5 / 11
                                            • First post
                                              Last post