@dafyre said:
@windso said:
- Add all your IT load wattages together. Done
Wattage of the Power Supplies, right?
- For 120V loads, take your server currents and multiply them all by 120V. If you have three phases, the process is the same: take all the currents, add together, multiply by 120V. Done!
What do you mean by server currents?
Current is amps. My question about the wattage is do you go by the labeled wattage of the power supply, or do you need to calculate the actual operating load?
-
Server Current is the force of the flowing servers in the computational stream.
-
@dafyre , good point, I edit the wording. See above. Really I mean current on each phase. Poorly worded. Sorry!
-
@scottalanmiller said:
Server Current is the force of the flowing servers in the computational stream.
Don't try to answer electrical questions with IT answers. lol
-
@scottalanmiller -- Mind = Blown
-
@dafyre Cha-ching!
-
@art_of_shred Actual operating load is the most practical.
-
@JColeKen said:
@art_of_shred Actual operating load is the most practical.
How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?
-
@JColeKen said:
@art_of_shred Actual operating load is the most practical.
Is there a simple percentage to use there as a ballpark figure?
-
@coliver said:
@JColeKen said:
@art_of_shred Actual operating load is the most practical.
How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?
An ammeter works great if you have one and want real numbers.
-
@art_of_shred 70-80% is a safe bet. Sometimes it is lower, but that is typically what I default to when sizing.
-
@art_of_shred said:
@coliver said:
@JColeKen said:
@art_of_shred Actual operating load is the most practical.
How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?
An ammeter works great if you have one and want real numbers.
Even in the afternoon or do you have to switch to a PMmeter?
-
Yes! These can be somewhat inexpensive. We usually see IT equipment running at 60% or less of nameplate rating. The challenge we have when sizing a UPS or PDU, and you will have too, is that generic rules always bite you at some point. If you are the exception, you risk taking down everything.
Keep in mind that sizing a UPS or PDU at less than 80% or 100% utilization is a good thing. UPSs and PDUs are like the breakers feeding your Christmas tree lights - Once you add too much, the lights go off!
-
@scottalanmiller Lolz
-
@scottalanmiller said:
@art_of_shred said:
@coliver said:
@JColeKen said:
@art_of_shred Actual operating load is the most practical.
How would you measure this in an environment without power monitoring? Or is it basically a guess at that point?
An ammeter works great if you have one and want real numbers.
Even in the afternoon or do you have to switch to a PMmeter?
Once again sporting your prowess in all things electrical. I defer to your expertise...
-
Couple of ones that might be more home oriented than business:
- Do you have any plans to get into the home battery market, like Tesla? (or are you already) These are the backup batteries that you can charge from solar and then power your home from (or use as a backup for if the power is out).
- What would you recommend in the prosumer market for IT pros or technically minded folks to use at home?
-
@windso said:
Yes! These can be somewhat inexpensive. We usually see loads running at 60% or less of nameplate rating. The challenge we have, and you will have too, is that generic rules always bite you at some point. If you are the exception, you risk taking down everything.
Keep in mind that sizing a circuit at less than 80% or 100% is a good thing. You never want to completely oversize, but UPSs and PDUs are like the breakers feeding your Christmas tree lights - Once you add too much, the lights go off!
Just to clarify, I thought that was worded a little confusingly. You never want your load to equal or surpass your protection. Ideally, your expected amp load should only be about 80% of your protection's full capacity. Otherwise, you can exceed its ability to protect and either diminish its performance or nullify the protection altogether.
-
That didn't sound good when I read it, so keep your mind out of the gutter.
-
@art_of_shred said:
That didn't sound good when I read it, so keep your mind out of the gutter.
Too late.
-
Are any of your PDUs capable of being remotely managed? So we can power stuff on / off remotely?