      scottalanmiller @donaldlandru
      last edited by

      @donaldlandru said:

      The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

      Size of the pie can be misleading. Absolute cost is what would matter in this instance.

      donaldlandruD 1 Reply Last reply Reply Quote 0
      • donaldlandruD
        donaldlandru @scottalanmiller
        last edited by donaldlandru

        @scottalanmiller said:

        @donaldlandru said:

        The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

        Size of the pie can be misleading. Absolute cost is what would matter in this instance.

        200w 24/7 @ $0.12 KWh is $211/annually

        This server is using 4% of the UPS, if I take that as one time that is $200 worth of UPS.

        DashrenderD 1 Reply Last reply Reply Quote 0
        • DashrenderD
          Dashrender @donaldlandru
          last edited by

          @donaldlandru said:

          @scottalanmiller said:

          @donaldlandru said:

          The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

          Size of the pie can be misleading. Absolute cost is what would matter in this instance.

          200w 24/7 @ $0.12 KWh is $211/annually

          Why does 200w seem so low?

          scottalanmillerS donaldlandruD 2 Replies Last reply Reply Quote 0
          • scottalanmillerS
            scottalanmiller @Dashrender
            last edited by

            @Dashrender said:

            @donaldlandru said:

            @scottalanmiller said:

            @donaldlandru said:

            The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

            Size of the pie can be misleading. Absolute cost is what would matter in this instance.

            200w 24/7 @ $0.12 KWh is $211/annually

            Why does 200w seem so low?

            That feels very low. You've got dual procs I assume, that's normally over 200W alone. Then the PSU and UPS overhead. The power of the SSDs, memory, fans, etc. It adds up. Can't imagine getting in under 300-400W.

            DashrenderD 1 Reply Last reply Reply Quote 0
            • DashrenderD
              Dashrender @scottalanmiller
              last edited by

              @scottalanmiller said:

              @Dashrender said:

              @donaldlandru said:

              @scottalanmiller said:

              @donaldlandru said:

              The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

              Size of the pie can be misleading. Absolute cost is what would matter in this instance.

              200w 24/7 @ $0.12 KWh is $211/annually

              Why does 200w seem so low?

              That feels very low. You've got dual procs I assume, that's normally over 200W alone. Then the PSU and UPS overhead. The power of the SSDs, memory, fans, etc. It adds up. Can't imagine getting in under 300-400W.

              Currently he has 2 or no drives in the server, but that will change when he adds the SSDs. So I suppose it's possible with a single Proc and no drives.

              scottalanmillerS donaldlandruD 2 Replies Last reply Reply Quote 0
              • scottalanmillerS
                scottalanmiller @Dashrender
                last edited by

                @Dashrender said:

                @scottalanmiller said:

                @Dashrender said:

                @donaldlandru said:

                @scottalanmiller said:

                @donaldlandru said:

                The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                200w 24/7 @ $0.12 KWh is $211/annually

                Why does 200w seem so low?

                That feels very low. You've got dual procs I assume, that's normally over 200W alone. Then the PSU and UPS overhead. The power of the SSDs, memory, fans, etc. It adds up. Can't imagine getting in under 300-400W.

                Currently he has 2 or no drives in the server, but that will change when he adds the SSDs. So I suppose it's possible with a single Proc and no drives.

                But a single proc and no drives isn't what he'd be running 🙂

                1 Reply Last reply Reply Quote 0
                • scottalanmillerS
                  scottalanmiller
                  last edited by

                  And 128GB of RAM alone draws a bit.

                  1 Reply Last reply Reply Quote 0
                  • donaldlandruD
                    donaldlandru @Dashrender
                    last edited by

                    @Dashrender said:

                    @donaldlandru said:

                    @scottalanmiller said:

                    @donaldlandru said:

                    The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                    Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                    200w 24/7 @ $0.12 KWh is $211/annually

                    Why does 200w seem so low?

                    With the assumption of 100% to the psu (450 watts) we are at just shy of $500 year for power which is noteworthy

                    scottalanmillerS 1 Reply Last reply Reply Quote 0
                    • scottalanmillerS
                      scottalanmiller @donaldlandru
                      last edited by

                      @donaldlandru said:

                      @Dashrender said:

                      @donaldlandru said:

                      @scottalanmiller said:

                      @donaldlandru said:

                      The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                      Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                      200w 24/7 @ $0.12 KWh is $211/annually

                      Why does 200w seem so low?

                      With the assumption of 100% to the psu (450 watts) we are at just shy of $500 year for power which is noteworthy

                      Only a single PSU?

                      DashrenderD donaldlandruD 2 Replies Last reply Reply Quote 1
                      • DashrenderD
                        Dashrender @scottalanmiller
                        last edited by

                        @scottalanmiller said:

                        @donaldlandru said:

                        @Dashrender said:

                        @donaldlandru said:

                        @scottalanmiller said:

                        @donaldlandru said:

                        The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                        Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                        200w 24/7 @ $0.12 KWh is $211/annually

                        Why does 200w seem so low?

                        With the assumption of 100% to the psu (450 watts) we are at just shy of $500 year for power which is noteworthy

                        Only a single PSU?

                        Maybe you go single PSU when you are looking at two servers.

                        If you go to a single server, I'd double it up if possible.

                        1 Reply Last reply Reply Quote 0
                        • donaldlandruD
                          donaldlandru @scottalanmiller
                          last edited by

                          @scottalanmiller said:

                          @donaldlandru said:

                          @Dashrender said:

                          @donaldlandru said:

                          @scottalanmiller said:

                          @donaldlandru said:

                          The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                          Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                          200w 24/7 @ $0.12 KWh is $211/annually

                          Why does 200w seem so low?

                          With the assumption of 100% to the psu (450 watts) we are at just shy of $500 year for power which is noteworthy

                          Only a single PSU?

                          Redundant PSU, but it would be foolish (and not sure if even possible) to exceed the limit of one supply

                          scottalanmillerS 1 Reply Last reply Reply Quote 0
                          • scottalanmillerS
                            scottalanmiller @donaldlandru
                            last edited by

                            @donaldlandru said:

                            @scottalanmiller said:

                            @donaldlandru said:

                            @Dashrender said:

                            @donaldlandru said:

                            @scottalanmiller said:

                            @donaldlandru said:

                            The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                            Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                            200w 24/7 @ $0.12 KWh is $211/annually

                            Why does 200w seem so low?

                            With the assumption of 100% to the psu (450 watts) we are at just shy of $500 year for power which is noteworthy

                            Only a single PSU?

                            Redundant PSU, but it would be foolish (and not sure if even possible) to exceed the limit of one supply

                            Absolutely, but the second one draws power when not in use. Not a ton, but some.

                            donaldlandruD 1 Reply Last reply Reply Quote 0
                            • donaldlandruD
                              donaldlandru @scottalanmiller
                              last edited by

                              @scottalanmiller said:

                              @donaldlandru said:

                              @scottalanmiller said:

                              @donaldlandru said:

                              @Dashrender said:

                              @donaldlandru said:

                              @scottalanmiller said:

                              @donaldlandru said:

                              The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                              Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                              200w 24/7 @ $0.12 KWh is $211/annually

                              Why does 200w seem so low?

                              With the assumption of 100% to the psu (450 watts) we are at just shy of $500 year for power which is noteworthy

                              Only a single PSU?

                              Redundant PSU, but it would be foolish (and not sure if even possible) to exceed the limit of one supply

                              Absolutely, but the second one draws power when not in use. Not a ton, but some.

                              My power consumption comes from both looking the my apc pdus and using a kill a watt meter before sizing the UPS.

                              I've noticed mine automatically load balances on the PSU at about 50%

                              1 Reply Last reply Reply Quote 0
                              • donaldlandruD
                                donaldlandru @Dashrender
                                last edited by

                                @Dashrender said:

                                @scottalanmiller said:

                                @donaldlandru said:

                                • Being 24/7 means I can't drop the whole thing for maintenance.

                                How much maintenance do you do? What is the annual downtime caused by VMware? Only VMware and hardware maintenance is assisted by having the second server.

                                Assuming a non DFRS file server, that would be assisted by this as well.

                                @donaldlandru , you said you have 7 servers. can't you install a DC on one of those? Are any of those virtualized or are they all bare metal?

                                2 servers are client owned hardware we have zero control over. I believe these are KVM.

                                2 more are the servers on topic here

                                Finally 3 servers are the "development" silo. With resource reservations I could put a domain controller and possibly a couple other services as well. Every resource used here detracts from revenue that can be generated from box, not that the business is keeping track but I am.

                                So yes I could use this for limited services

                                1 Reply Last reply Reply Quote 0
                                • donaldlandruD
                                  donaldlandru @Dashrender
                                  last edited by

                                  @Dashrender said:

                                  @scottalanmiller said:

                                  @Dashrender said:

                                  @donaldlandru said:

                                  @scottalanmiller said:

                                  @donaldlandru said:

                                  The UPS and power do come into play but at 200 watts (one server in question) is a small piece of the pie

                                  Size of the pie can be misleading. Absolute cost is what would matter in this instance.

                                  200w 24/7 @ $0.12 KWh is $211/annually

                                  Why does 200w seem so low?

                                  That feels very low. You've got dual procs I assume, that's normally over 200W alone. Then the PSU and UPS overhead. The power of the SSDs, memory, fans, etc. It adds up. Can't imagine getting in under 300-400W.

                                  Currently he has 2 or no drives in the server, but that will change when he adds the SSDs. So I suppose it's possible with a single Proc and no drives.

                                  One of the drives I am looking at has information I think are not correct. https://www.sandisk.com/home/ssd/extreme-pro-ssd claims .15watts while active. The Samsung data center model is the other one which claims 3.4watts while active. Assuming the 3.4 that is 28 watts per server added

                                  1 Reply Last reply Reply Quote 0
                                  • scottalanmillerS
                                    scottalanmiller
                                    last edited by

                                    SSDs save a TON on power over Winchester drives. That's for sure.

                                    donaldlandruD 1 Reply Last reply Reply Quote 1
                                    • donaldlandruD
                                      donaldlandru @scottalanmiller
                                      last edited by

                                      @scottalanmiller said:

                                      SSDs save a TON on power over Winchester drives. That's for sure.

                                      I agree there. I'd have to look it up but willing to bet taking out the two 15k, adding the ssd will still be a net power savings

                                      1 Reply Last reply Reply Quote 0