      @thanksajdotcom said:

      @scottalanmiller said:

      Why is your server room at 17 anyway? That is far, far below recommended temperatures.

      And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

      Yup, I'd look at raising that at least to 25.

      IT-ADMINI 1 Reply Last reply Reply Quote 0
      • scottalanmillerS
        scottalanmiller
        last edited by

        Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

        thanksajdotcomT 1 Reply Last reply Reply Quote 0
        • thanksajdotcomT
          thanksajdotcom @scottalanmiller
          last edited by

          @scottalanmiller said:

          Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

          Wow, that's 86-90F. That seems very warm!

          coliverC scottalanmillerS 2 Replies Last reply Reply Quote 0
          • IT-ADMINI
            IT-ADMIN @scottalanmiller
            last edited by

            @scottalanmiller said:

            @thanksajdotcom said:

            @scottalanmiller said:

            Why is your server room at 17 anyway? That is far, far below recommended temperatures.

            And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

            Yup, I'd look at raising that at least to 25.

            the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

            coliverC scottalanmillerS 2 Replies Last reply Reply Quote 0
            • coliverC
              coliver @thanksajdotcom
              last edited by

              @thanksajdotcom said:

              @scottalanmiller said:

              Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

              Wow, that's 86-90F. That seems very warm!

              We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

              thanksajdotcomT scottalanmillerS 2 Replies Last reply Reply Quote 0
              • coliverC
                coliver @IT-ADMIN
                last edited by

                @IT-ADMIN said:

                @scottalanmiller said:

                @thanksajdotcom said:

                @scottalanmiller said:

                Why is your server room at 17 anyway? That is far, far below recommended temperatures.

                And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

                Yup, I'd look at raising that at least to 25.

                the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

                Your server room should have independent air conditioning. Keeping it around 20-25 C should be fine.

                scottalanmillerS 1 Reply Last reply Reply Quote 1
                • thanksajdotcomT
                  thanksajdotcom @coliver
                  last edited by

                  @coliver said:

                  @thanksajdotcom said:

                  @scottalanmiller said:

                  Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                  Wow, that's 86-90F. That seems very warm!

                  We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                  I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                  scottalanmillerS 1 Reply Last reply Reply Quote 0
                  • scottalanmillerS
                    scottalanmiller @thanksajdotcom
                    last edited by

                    @thanksajdotcom said:

                    Wow, that's 86-90F. That seems very warm!

                    It sure does, because IT has this cultural obsession with thinking only in terms of the servers themselves and not holistically for the business. It's "IT at any cost" thinking. That and poor airflow forces datacenters to go with super cold air to make up for heated air pockets.

                    But servers do not need the cold air that IT generally assumes. That's a myth that just keeps getting repeated. Good airflow and holistic business thinking put the optimum temperatures much higher in cases where the cold air is not essentially free (like Scotland.)

                    1 Reply Last reply Reply Quote 0
                    • scottalanmillerS
                      scottalanmiller @coliver
                      last edited by

                      @coliver said:

                      @IT-ADMIN said:

                      @scottalanmiller said:

                      @thanksajdotcom said:

                      @scottalanmiller said:

                      Why is your server room at 17 anyway? That is far, far below recommended temperatures.

                      And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

                      Yup, I'd look at raising that at least to 25.

                      the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

                      Your server room should have independent air conditioning. Keeping it around 20-25 C should be fine.

                      What matters is keeping it consistent, not the temp itself.

                      1 Reply Last reply Reply Quote 2
                      • scottalanmillerS
                        scottalanmiller @IT-ADMIN
                        last edited by

                        @IT-ADMIN said:

                        @scottalanmiller said:

                        @thanksajdotcom said:

                        @scottalanmiller said:

                        Why is your server room at 17 anyway? That is far, far below recommended temperatures.

                        And if you're dealing with high humidity as it is, this will only amplify the condensation problem by keeping the temperature lower...

                        Yup, I'd look at raising that at least to 25.

                        the problem is the high temperature we have in qatar, usually 46 - 38 C, so if i raise the temperature, i risk to kill the servers

                        That's NOT how air conditioning works. The temperature outside has nothing to do with the temperature inside. If you set it to 17, it is 17 no matter what the temp is outside. If you set it to 25, it is the same 25 as for any of us. Your 25 is not hotter than ours. What DOES matter is that the cost of cooling from 46 to 17 is much, much higher than cooling from 25 to 17. So the price for going unnecessarily low is more for you.

                        1 Reply Last reply Reply Quote 1
                        • scottalanmillerS
                          scottalanmiller @coliver
                          last edited by

                          @coliver said:

                          @thanksajdotcom said:

                          @scottalanmiller said:

                          Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                          Wow, that's 86-90F. That seems very warm!

                          We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                          We've done these tests (nonvoluntarily) with HP servers and they ran happily towards 160F!! But I would not recommend it since humans can't go in the room to replace parts.

                          1 Reply Last reply Reply Quote 0
                          • scottalanmillerS
                            scottalanmiller @thanksajdotcom
                            last edited by

                            @thanksajdotcom said:

                            @coliver said:

                            @thanksajdotcom said:

                            @scottalanmiller said:

                            Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                            Wow, that's 86-90F. That seems very warm!

                            We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                            I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                            Although it is opposite, for electronics which are air cooled, high humidity increases cooling potential. For humans which are evaporation cooled, humidity decreases cooling potential.

                            thanksajdotcomT 1 Reply Last reply Reply Quote 0
                            • scottalanmillerS
                              scottalanmiller
                              last edited by

                              IBM has shown that running at 37C consistently is far better for your gear than bouncing around between 15C and 20C.

                              1 Reply Last reply Reply Quote 0
                              • scottalanmillerS
                                scottalanmiller
                                last edited by

                                Moving to SSDs actually makes it:

                                • Easier to cool as there is less heat generated and less power drawn.
                                • Temps can be higher than before.
                                • Fluctuations are not as big of a risk.

                                You can potentially save a lot of money with SSD for various reasons.

                                1 Reply Last reply Reply Quote 1
                                • thanksajdotcomT
                                  thanksajdotcom @scottalanmiller
                                  last edited by

                                  @scottalanmiller said:

                                  @thanksajdotcom said:

                                  @coliver said:

                                  @thanksajdotcom said:

                                  @scottalanmiller said:

                                  Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                                  Wow, that's 86-90F. That seems very warm!

                                  We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                                  I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                                  Although it is opposite, for electronics which are air cooled, high humidity increases cooling potential. For humans which are evaporation cooled, humidity decreases cooling potential.

                                  Fair enough...still, water on a board due to condensation is a risk.

                                  scottalanmillerS 1 Reply Last reply Reply Quote 0
                                  • scottalanmillerS
                                    scottalanmiller @thanksajdotcom
                                    last edited by

                                    @thanksajdotcom said:

                                    @scottalanmiller said:

                                    @thanksajdotcom said:

                                    @coliver said:

                                    @thanksajdotcom said:

                                    @scottalanmiller said:

                                    Intel and IBM tests in similar weather conditions (New Mexico instead of Qatar) years ago put optimum efficiency of the datacenter closer to 30-32.

                                    Wow, that's 86-90F. That seems very warm!

                                    We studied that project in grad school. It was pretty cool how they set it up. As long as humidity didn't get too high you could have ambient temperatures of ~100F before things started to fail.

                                    I guess that makes sense. I mean, as a mostly-human being, Syracuse during the summer is often infinitely harder to handle than Dallas ever was due to how humidity affects perception of temperature. I guess it wouldn't be THAT different to electronics.

                                    Although it is opposite, for electronics which are air cooled, high humidity increases cooling potential. For humans which are evaporation cooled, humidity decreases cooling potential.

                                    Fair enough...still, water on a board due to condensation is a risk.

                                    Oh yes, you can't let there be water, ever.

                                    1 Reply Last reply Reply Quote 0
                                    • IT-ADMINI
                                      IT-ADMIN
                                      last edited by

                                      i go to the server room to raise the tempreture, i realize that the remote controller is missing 😲

                                      scottalanmillerS 1 Reply Last reply Reply Quote 1
                                      • scottalanmillerS
                                        scottalanmiller @IT-ADMIN
                                        last edited by

                                        @IT-ADMIN said:

                                        i go to the server room to raise the tempreture, i realize that the remote controller is missing 😲

                                        Look in the couch. It is always in the couch.

                                        IT-ADMINI 1 Reply Last reply Reply Quote 2
                                        • scottalanmillerS
                                          scottalanmiller
                                          last edited by

                                          You know it is an enterprise HVAC system when you have a remote 🙂

                                          1 Reply Last reply Reply Quote 1
                                          • IT-ADMINI
                                            IT-ADMIN @scottalanmiller
                                            last edited by

                                            @scottalanmiller said:

                                            @IT-ADMIN said:

                                            i go to the server room to raise the tempreture, i realize that the remote controller is missing 😲

                                            Look in the couch. It is always in the couch.

                                            lol, it is not the TV remote controller, i'm talking about the AC